CEEforms are ridiculously over spec'd for the application although perfectly acceptable.
Yes, just a bit over specced
As to the concerns about incorrect application of these connectors. I say use them properly as I have come across so many silly applications, some of which are potentially dangerous:
1P power to a van using a red 3PNE, L2 & L3 had a short in the socket, in the van was a relay to inhibit the starter solenoid:
View attachment 154952
with the van was a cable with a blue plug and red socket which worked successfully for several years. On a site the temp electric supplier had been asked to provide a 16A supply and seeing a red plug applied 3ph.
Ouch !
I've seen 32/3 being used as 2x1ph (2xL & 2xN with common earth).
Both of the above did a lot of damage.
I bet
At a previous job, we got a phone call from a customer asking about using a widowmaker (not that they used the term) to power up their building from the neighbours generator. I explained to them that this was a bad idea for two reasons :
- Firstly it's stupidly dangerous
- Secondly they have their circuits split over 3 phases - and no I don't know which 13A socket you'd need to plug into in order to power up the server room.
I then went on to say that they should get an electrician in to fit a 3 phase input connector and a changeover switch - which is what they did. On the morning of the pre-announced power cut, they called to say that they'd tried plugging in power from next door but it had just tripped next-doors genny. I set off, picking up my portable genny en route - with extension leads to reach the server room and connect the UPS to it as we'd done a few times before.
When I got there, they were powered up and the neighbour said that they'd found two problems : the inlet was incorrectly wired, and there was no neutral in their connecting lead.
I got chatting with one of the guys from next door. They sell and rent electrically powered mini diggers, some of them with remote control, that can be used in places where an engine powered unit could not be used. They didn't need a neutral for their machines, so they saved money by not having a neutral in their connecting cables. I think I said something about the risks involved, but they seemed to think that as they supervise their stuff it would be OK. I could just imagine someone needing power, seeing a 5 pin socket spare, and plugging in - with the potential for damage caused by a missing neutral.
But at least I had persuaded them to stop using a widowmaker themselves and fit an inlet & switch
Using a 16/3 for a boiler 'shouldn't' cause any problem if someone tried to use the socket to supply a3ph device but applying 3ph to the boiler plug would very likely damage the pcb.
3 phase isn't around so the only way it would happen is if someone brought in a genny - but that's not likely either as I can't see us hosting any events with that sort of power requirement. In any case, tucking a relay in the boiler control box powered from the demand signal would obviate that risk - and would be needed for some boilers which need volt free switching. But thinking about it, I strongly suspect that all there is in most boilers is a rectifier, resistor, and zener (or other clamp) to derive a low level signal from the mains level input.
Klix is a much better option but do you not require 5 poles? LNE supply, demand & pump.
Pump is externally controlled.
So use a red one then.
"Maximum" is not the same as "mandatory".
I never said it was. And I said using a red one was the safest option.
This started when it was suggested I use a blue one as there's only 240V present, and I queried that. At which point you butted in with "F*S this is a church hall"
If the thread is boring you, then just stop reading it - some of us are having a rational discussion.
As Sunray points out in a later post, you never know who might turn up.