If you can make a boxing with the cables more than 50mm from the surface I can't see any major issues.
im not quite sure what you mean mate?
you mean box them in instead of having them exposed?
Last edited:
If you can make a boxing with the cables more than 50mm from the surface I can't see any major issues.
Which part?well id imagine he takes responsibility for the installation is the gist
Indeed - but, interestingly (maybe 'very surprisingly'?), if we are talking about England, and if the tails are to be connected to an existing CU, then I'm not sure by what criterion their replacement would be notifiable work!Plus, of course, there is virtually the only legal part of the work (apart from doing the work to ensure safety) of notifying the Local Authority.
i mean a certificate or whatever its called, as required by the building inspector. Its a brand new house so everthing needs to be certified
Which part?
the design ?
the construction ?
the inspection and testing ?
or some combination of those three things ?
The problem is that if you or someone else installs things which are not compliant, it's then far too late when this person arrives to 'sign off' whatever it is they are taking responsibility for. The only option then would be rip it all out and start again.
That is why all questions relating to this installation must be directed to this person - and not random people on a forum who know nothing about this installation or the circumstances in which it being installed.
View attachment 184524
If you discuss the work with your electrician first, and he's happy for you to do the donkey work to his specification (and I'm sure he will be MORE than happy for you to do the donkey work) then it's down to him.
Plus, of course, there is virtually the only legal part of the work (apart from doing the work to ensure safety) of notifying the Local Authority.
If your friend's brother is not registered to do this through one of the schemes, then YOU must notify them before the work commences and satisfy them that the work will be carried to their - LA's - satisfaction.
Indeed - but, interestingly (maybe 'very surprisingly'?), if we are talking about England, and if the tails are to be connected to an existing CU, then I'm not sure by what criterion their replacement would be notifiable work!
Kind Regards, John
Yes, I missed that. If it's a brand new electrical installation, I would have expected the person who specified and installed the CU to also specify (and install) the tails!its a new house John, so i assume you meant in a house wired previously?
A switchfuse is required if the tails are more than 3m long. An isolator on it's own is not suitable.
As someone else mentioned, this isn't strictly true. It depends entirely on the requirement from the local DNO, but for example UKPN were not concerned about longer than 3m last time I spoke with them. Their suggestion was to use SWA or similar but that's it.
Given that it's so arbitrary (as well as 'daft'), I suppose there's bound to be appreciable variation.I've got this funny feeling SEB stipulated 3m for tails, but could be 5m under certain conditions, like an upstairs flat, but I could be really wrong about that. Can't remember, it was many years ago.