Just been round to a mates house to find his shower is a 9.5kw shower on a 32amp cartridge fuse! Its on a 10mm csa cable, but 32a fuse.
How come it has not blown by now??
9.5kw roughly equates to 40A. A 30A cartridge fuse does not blow at exactly 30A, it should disconnect within 1 hour at approximately 1.45x its rating. At 40A it will take a very long time if it blows at all. It is however bad practice to overload a circuit protective device.
Would a 32amp MCB, RCBO be better in the same position as they don't have the heating/cooling of wired protection ( I know it should be about 45a) ?
I would suggest he changed it though.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local