I'm doing my cable calcs to rewire my house (will one day get to doing the actual wiring!!!) and I've worked out the ring for my downstairs sockets will be 90m... This sounds excessive to me, but when I measure and remeasure it comes out the same. I'm taking into account the proper places where I can drill/notch joists, so sometimes the routes are a little longer than would be electrically ideal.
The OSG reckons that 2.5mm T&E, clipped direct, on a 32A mcb, RCD protected, with TN-S supply, allows for a 106m ring so I should be OK, it just feels like cutting it a little close when most of my other circuits are coming out with a massive margin to spare!
3-bed house, ring covers living room, hallway, dining room.
Concrete floors, so cable drops from ceiling (approx 2.5m ceiling height so each drop adds between 4m and 5m depending on where it is)
2 drops in hallway, 4 drops in dining room and 5 in living room (so at least 44m of cable is purely for the drops).
Total floor area served about 60m^2