220A is the figure for 5 seconds but you can't get 220A - you only have 64 (230/3.57).The over protective device for the 10mm T+E sub-main is a 50A 1361 fuse. When i phoned the helpful bloke at the NICEIC he said to use BS88-2 fuse to work out the prospective fault current as per table in the bible. Therefore using 220A as that figure, and working out the adiabatic equation you get the figure of 4.91mm. Hence why it has been TT'd (i presume).
So the supply to the second doesn't flow through the first.The second D.B has been tapped off of the top of the first D.B's RCD and into its own RCD upfront.
Do you mean the second DB's earth is connected to the electrode?The earth has been segregated in the first D.B (as it's now a TT). The cpc for the ongoing feed to the second D.B has been terminated into the earth bar in the first D.B.
Is it not already? Dependent on the answer to the previous question.I have talked to the client and i am going to TT the second D.B and Obviously segregate the incoming earth in that board.
What will you do if it is more than 3.57?I can assure you that it really is a true EFLI!!
Will be interesting to see what figure o get when i bang the first rod in for the second D.B!
Yes, indeed.Job done.
What is the Ze at the origin?
That's always good.I'm going for a beer!