I'm not so sure. The problem with loop testing is that the nature of it is such there is no way of 'checking the zero'. It is therefore far from impossible that everything could have shifted up or down (which would not take much of an electronic malfunction or maladjustment), such that a zero loop impedance, if one could emulate it, would be measured/displayed as non-zero, and all readings would be XΩ above or below the true value.Extraordinarily unlikely, I would have thought.As I said, all that proves is that the slope of the true/displayed value has not changed. Although it's probably not a very likely scenario, the finding that addition of a particular resistance results in the same change in indicated reading as it 'always has' does not preclude the possibility that the meter is giving incorrect absolute readings.
As I said (in the bit before my "However..." that you have quoted), I would personally not normally do it with more than one value of resistance (although I guess that I would probably try a different resistance if the first one did not give the expected answer - but that hasn't happened yet). I don't know how 'properly' or exhaustively the calibration people check loop impedance measurement (they may do no more than we are discussing!) but one might like to think that 'proper checking' would involve more than one loop impedance (or incremental loop impedance).Two would give you 3 different ΔΩ. Three would give you 7, which I submit would be both unnecessary and tedious to work through.However, having said that, it would not be such a bad idea to use two or more different added resistances, particularly given that a malfunction would not inevitably be linear in relation to incremental resistance.
Kind Regards, John