Hi, having successfully replaced a defunct shower with a nice shiny new one, with some reassurance from you guys (Another 6mm or 10mm shower cable question), I was wandering what your thoughts were on the following.
The existing shower circuit is fed with a 45A MCB in a circa 2003 16 way MK Sentry CU. It is not split load as is, although does have 2 neutral bars joined together by a hard link. There is no RCD protection.
Whilst visiting B&Q today there was a twin pole 40A 30mA MK RCD for Sentry boards sitting in Bargain Corner, so after a bit of a think I bought it. Having got it home I've found that the accompanying paperwork was non de script to say the least so have been trawling the net looking for some answers.
I gather that in a split load board, the RCD is fed from the 'switched' side of the incoming supply via a cable link to the top right pole, the top left pole of the RCD connects to the main neutral bar via a link cable, bottom left pole connects to 'protected' neutral bar via another cable link, and bottom right pole feeds buzz bar which in turn supplies the MCB's on the protected side.
So the questions.....
1) Having read a reply from Adam_121 on another topic I gather that you still need a MCB to run a circuit protected by RCD.
In a non split board where is best to site the RCD and MCB given that only one MCB is to be used with the RCD for the shower?
I'm guessing that far right of the board would be best so that the buzz bar can be cut in front of the RCD, but leaving a slot for the MCB after the RCD. MK, by the way, sell a split load kit that supplies the wire links. 14 ways are usable in the CU after the incoming. At present only 7 are used and nothing is wired into the second neutral bar so link could be removed and used as protected for RCD.
2) Is it actually OK to cut the buzz bar in the first place? I'm assuming that if MK sell a kit then it must be ok. I think the board is a 'K' Series.
3) The current MCB is 45A but RCD is 40A. Is this a mis-match? The Triton Zante (T80si) states it can be 40 or 45 on the MCB. Install is on 6mm clipped run of 5 metres, last meter through UN-insulated stud wall so available amperage should be in realms of 46A or thereabouts. Shower is 9.5Kw - 240V, 8.7Kw - 230V. A 40A MCB is only a few quid if so.
In hind site I'm guessing buying a higher Amp RCD would have been better and made the board properly split load, or a RCBO, but it was an impulse buy and I'm stuck with it. What do you reckon?
Thanx again in advance for your replys.
The existing shower circuit is fed with a 45A MCB in a circa 2003 16 way MK Sentry CU. It is not split load as is, although does have 2 neutral bars joined together by a hard link. There is no RCD protection.
Whilst visiting B&Q today there was a twin pole 40A 30mA MK RCD for Sentry boards sitting in Bargain Corner, so after a bit of a think I bought it. Having got it home I've found that the accompanying paperwork was non de script to say the least so have been trawling the net looking for some answers.
I gather that in a split load board, the RCD is fed from the 'switched' side of the incoming supply via a cable link to the top right pole, the top left pole of the RCD connects to the main neutral bar via a link cable, bottom left pole connects to 'protected' neutral bar via another cable link, and bottom right pole feeds buzz bar which in turn supplies the MCB's on the protected side.
So the questions.....
1) Having read a reply from Adam_121 on another topic I gather that you still need a MCB to run a circuit protected by RCD.
In a non split board where is best to site the RCD and MCB given that only one MCB is to be used with the RCD for the shower?
I'm guessing that far right of the board would be best so that the buzz bar can be cut in front of the RCD, but leaving a slot for the MCB after the RCD. MK, by the way, sell a split load kit that supplies the wire links. 14 ways are usable in the CU after the incoming. At present only 7 are used and nothing is wired into the second neutral bar so link could be removed and used as protected for RCD.
2) Is it actually OK to cut the buzz bar in the first place? I'm assuming that if MK sell a kit then it must be ok. I think the board is a 'K' Series.
3) The current MCB is 45A but RCD is 40A. Is this a mis-match? The Triton Zante (T80si) states it can be 40 or 45 on the MCB. Install is on 6mm clipped run of 5 metres, last meter through UN-insulated stud wall so available amperage should be in realms of 46A or thereabouts. Shower is 9.5Kw - 240V, 8.7Kw - 230V. A 40A MCB is only a few quid if so.
In hind site I'm guessing buying a higher Amp RCD would have been better and made the board properly split load, or a RCBO, but it was an impulse buy and I'm stuck with it. What do you reckon?
Thanx again in advance for your replys.