So 1mm² T/E will carry any current that will go through a 100A service fuse, will it, for the amount of time that the service fuse will pass it, without getting hot enough to start a fire?If a breaker does jam closed in a fault current situation though (quite unlikely), in a house, then the fuse provided by the electricity supply company should opperate before anything actually bursts into flame
Probably not if the fault is at the far end of the circuit , and impedances are high, currents lower and disconnection times longer and dispated I²t higher... I must admit I based my thinking on fault current of pretty high magnatude (a couple of ka), the numbers work then and nothing catches fire, unfortunatly in my haste to be clever I forgot to consider what would happen if the fault was a tad more than 2' from the DB
If the fault current is lower then due to the impedance of the circuit then the protective device in the CU should be able to cope, depending on it's Icu rating.