Hi,

I have a radial circuit on a 20A MCB in the C/Unit.

This circuit runs directly to and feed only an air conditioning unit with ratings:
Rated Curent (A)
Cooling - 12.0 (1.4-12.5)
Heating - 11.5 (2.3-14.0)

Input Power (Kw)
Cooling - 2.4 (0.5-3.0)
Heating - 2.2 (0.3-2.6)

Can you tell me if I can add one or two double sockets onto the circuit (not spurs) these will be situated in the second bedroom which currently only has one spur socket off the ring main.

many thanks
 
Sponsored Links
Why not extend the ring cct?

Or

Change the existing spurred socket to an FCU then power additional sockets from the load side.
 