I second that, so I'm glad you thanked Monkeh for the advice, because given that you proposed to put 2.5mm cable on a 32A breaker, and create a 16A ring final (not what the Wiring Regulations recognise), I think you're way out of your depth.I'd advise you get a couple of local electricians around and see what they think..
What did you plan to tell your local Building Control department would be the way you'd comply with Part P?
I second that, so I'm glad you thanked Monkeh for the advice, because given that you proposed to put 2.5mm cable on a 32A breaker, and create a 16A ring final (not what the Wiring Regulations recognise)
You dont need 3 RCDs in a row like that. You end up with 3 RCDs protecting the shed. In the event of a fault, the quickest RCD will trip. Not nessecarily the one closest to you. Its not dangerous, but bad design.
Cable to garage not RCD protected (it doesnt need to be) - this may need re-think in the house CU.
In the garage CU, use a mainswitch (not rcd), use a 6A MCB for the lighting, and RCBO for sockets, and an MCB for the shed circuit.
in the shed, use an RCD mainswitch.
They don't carry out design reviews, they want you to tell them how you will ensure that you will be making reasonable provision for safety etc.Essentially I was going to tell them exactly what I'd posted on here. I thought I could explain what I currently have and then what I propose to do.
No. 2.5mm² SWA cannot carry 32A, so you can't use a 32A breaker to protect it.32amp MCB - 2.5 mm sq SWA to shed
Not if it isn't properly done.I thought, by using LBC, I would still be doing all the work and still get it passed.
Yup.I have read on this forum somewhere that if the LBC then want the installation tested, it is something they have to do at their cost and cannot pass this on.
I fear your confidence is misplaced.I feel confident enough to carry out the installation
and shame on all the previous repliers for not picking up on this:
No. 2.5mm² SWA cannot carry 32A, so you can't use a 32A breaker to protect it.32amp MCB - 2.5 mm sq SWA to shed
No. 2.5mm² SWA cannot carry 32A, so you can't use a 32A breaker to protect it.
And you're not, and shame on all the previous repliers for not picking up on this:
32amp MCB - 2.5 mm sq SWA to shed
In that case overload protection is provided downstream, either by an FCU or by imposing a limit of 1 socket outlet.
In this case there is no such overload protection - the 2.5mm² would be supplying a CU.
Spurring off a ring final does not absolve you from considering the current carrying capacity of the 2.5mm² cable as installed. Method C is 27A, which is less than 2 x 13A.Its totally permissable to fit a dsso on a 2.5 spur on a ring final and as I have mentioned before its common practice to make this provision for a washing machine and dishwasher for example.
So stop there.Much of this sort of appliance coming in from abroad with CE markings and moulded 13A plugs is rated at 3KW or even 3.2KW at 220V. Doing the sums 3200/220=14.55A, So thats wrong.
Ditto.220/14.55=15.2ohms and 240V/15.2=15.7A or 3.7KW. and there is 2 of those plugged into a DSSO so thats wrong too
No it does not.as the 2.5mm is running at peaks of 31A on a cable rated at 28A tops and yet it still complies with the regs
Or until the socket overheats and fails, because 31A is in excess of the current that BS 1363 sockets are rated at.and works ok till the cable gets too hot and fails.
No it is not.I know I am making reference to unrelated regs but that does not change the fact that in some circumstances it is permissible to inadequately protect a 2.5mm cable with a 32A device, knowing that the following protection is inadequate too.