What a pile of poo this boiler is. It's only about 6 years old but in that time i have changed:
Fan assy 3 times
PCB twice
Temp sensor once.
Inlet/exhaust tube twice
Inlet/exhaust elbow once
The problems started with a failed fan PCB so I replaced it.
That lasted a couple of weeks. I found that the plastic exhaust tube had hardened and cracked, allowing condensation into the induction tube which would then drip directly onto the PCB.
I replaced the tube and the PCB and all was well for a year or so. Then the same thing happened again and this time I found that not only was the exhaust tube cracked again but the cast elbow was so corroded that it was holed and also allowing condensation into the induction tube.
A new elbow, new tube and new PCB and function was restored.
Another year and this time it appeared that the pressure differential switch was playing up. It took me a while to discover that there was so much sediment in the heat exchanger that it was blocked, causing the pressure problem. i removed, stripped and cleaned it and all was well again.
Next season the PCB failed. That lasted a year. Another PCB and also temp sensor as it had gone brittle and cracked.
Today the boiler has failed again. It's dead, no lights at all but there's power to the PCB. I haven't investigated yet, it might just be a fuse, but what a royal PITA this thing is. You can probably deduce from my forum name that I'm used to fixing complicated things but this is ridiculous.
Rant over.
What a pile of poo this boiler is. It's only about 6 years old but in that time i have changed:
Fan assy 3 times
PCB twice
Temp sensor once.
Inlet/exhaust tube twice
Inlet/exhaust elbow once
The problems started with a failed fan PCB so I replaced it.
That lasted a couple of weeks. I found that the plastic exhaust tube had hardened and cracked, allowing condensation into the induction tube which would then drip directly onto the PCB.
I replaced the tube and the PCB and all was well for a year or so. Then the same thing happened again and this time I found that not only was the exhaust tube cracked again but the cast elbow was so corroded that it was holed and also allowing condensation into the induction tube.
A new elbow, new tube and new PCB and function was restored.
Another year and this time it appeared that the pressure differential switch was playing up. It took me a while to discover that there was so much sediment in the heat exchanger that it was blocked, causing the pressure problem. i removed, stripped and cleaned it and all was well again.
Next season the PCB failed. That lasted a year. Another PCB and also temp sensor as it had gone brittle and cracked.
Today the boiler has failed again. It's dead, no lights at all but there's power to the PCB. I haven't investigated yet, it might just be a fuse, but what a royal PITA this thing is. You can probably deduce from my forum name that I'm used to fixing complicated things but this is ridiculous.