One more thought.
If the dimmer was operating into a transformer ( wound type ) the non sinusiodal waveform from the dimmer might be reacting in the coild of the transformer to produce high voltage low energy spikes. ( as per car ignition coil ).
Your meter may be showing the voltage of the spike.
Make up a load of two 230 bulbs connected in series and put this across where you find 400 volts. If they light you have a second phase involved or the incoming neutral is extremely suspect.
Stick a earth rod in wet ground and use that as a reference to measure the voltage on the incoming neutral. More than about 50 volts between neutral and the earth rod means the network hasa problem with their neutral.