I cannot see any effective earthing at the meter location.
There is no CPC taken from the cutout so it doesn't look like a PME system.
Is it a TT supply ?
Does it rely on that voltage operated earth leakage breaker for protection ?
If so then there is no protection as what appears to be the CPC of the wiring is connected to the grounded terminal and not ( as it should be, to the ungrounded end of the VOELB's coil. ( the small terminal at the top of the unit.
The "earth rod" connection looks like a bit of copper pipe driven into the ground. How long is it.