If there is enough height to the CU for RCBOs to be 'easily' installed, then that would be a theoretical possibility - although RCBOs are so much more expensive that MCBs that such an approach would probably not make sense unless you actually wanted RCBOs (which is not a bad idea!). Some would probably argue that doing that would change the CU enough that it counted as a replacement one, in which case it would have to have a metal case - but it looks as if yours might already be metal?I persume I couldn't just have the rhs mcbs replaced with RCBO's then, it would be a new Consumer Unit installed?.
A dual RCD CU (covering all circuits) would currently be quite a lot cheaper than an all-RCBO one - MCBs are typically £2-£3 each, whereas RCBOs are generally over £20 each (and RCDs perhaps about £30 each).Thanks John, all RCD protected would be nice so it looks like I'll have to start saving the pennies!. Yeh it is a metal consumer unit.
If you know him fairly well, you would presumably at least be fairly confident that he is not a 'cowboy', which unfortunately is not always the case with Yellow Pages etc.!I have a customer at work who I get on with very well who's and electrician, I may have to bend his ear next time I see him rather than going through the Yellow Pages.
It should be pointed out that RCDs are for personal protection.Main concern is the metal light fittings and metal oven are not RCD protected at the moment.
Indeed, provided that the fault is of sufficiently low impedance that enough current flows through it to trip an MCB. If the impedance is not that low, the 'touch voltage' is almost certainly not going to get high enough to represent a threat to life (for most people), although they might get a significant shock if they touch it and something (else) 'earthed'.....As it is now earthed, such a fault will result in disconnection of the supply by the MCB before anyone gets there.
Well, yes, it's supposed to be. Why would it not be (on a 6A circuit)?Indeed, provided that the fault is of sufficiently low impedance that enough current flows through it to trip an MCB.
Well, yes, but that's just saying "If things don't work as they should then things will not happen that should, and something that should not happen will".If the impedance is not that low, the 'touch voltage' is almost certainly not going to get high enough to represent a threat to life (for most people), although they might get a significant shock if they touch it and something (else) 'earthed'.
Not if the light body is live and unearthed.RCD protection would prevent more than a tiny persistent 'touch voltage' ever occurring.
As you know, the only requirement is that the fault current should be adequate to magnetically trip the RCD is the presence of a 'negligible' (aka 'zero') impedance L-E fault. If the Zs of a circuit is only just low enough for that, then any finite fault impedance will mean that the MCB will not trip magnetically and, if the fault impedance were sufficiently high, not necessarily ever trip.Well, yes, it's supposed to be. Why would it not be (on a 6A circuit)?
I don't really understand that comment. I was merely saying that if the circuit's Zs is compliant, then the R2 is going to be sufficiently low that the touch voltage of the exposed-c-p would never get up to what is regarded as a 'dangerous' level, no matter what the fault impedance.Well, yes, but that's just saying "If things don't work as they should then things will not happen that should, and something that should not happen will".
I was talking about the situation in which the light body is earthed - and persistently 'live' (because of an L-E fault) only to the extent of the VD in the CPC - say about 0.12V in the case of a 30mA RCD and a (very pessimistic) R2 of 4Ω.Not if the light body is live and unearthed.