OP, do you work with computers or legal matters?
I have suggested 16 kW because the heat loss is probably between 12 kW and 20 kW depending on how well insulated your house is.
But those figures are based on an outside temperature of -1 C and for the summer we don't expect many nights when it goes below 8 C so for a summer setting 16 kW is bound to be totally adequate and probably for the winter too depending on the actual heat loss.
But for the time being the whole purpose is to set the boiler to avoid this cycling as far as possible with a seriously oversized appliance.
The Megaflow does need to be fitted with the correct controls as required by the maker and the G3 regulations. But that does not prevent the cylinder temperature being monitored by the Vaillant cylinder temperature sensor if used with their smart controls.
Tony
I have suggested 16 kW because the heat loss is probably between 12 kW and 20 kW depending on how well insulated your house is.
But those figures are based on an outside temperature of -1 C and for the summer we don't expect many nights when it goes below 8 C so for a summer setting 16 kW is bound to be totally adequate and probably for the winter too depending on the actual heat loss.
But for the time being the whole purpose is to set the boiler to avoid this cycling as far as possible with a seriously oversized appliance.
The Megaflow does need to be fitted with the correct controls as required by the maker and the G3 regulations. But that does not prevent the cylinder temperature being monitored by the Vaillant cylinder temperature sensor if used with their smart controls.
Tony