Scenario : 8kW shower, Ambient temp 30degC, clipping direct ref method 1, thermal insulation 400mm, touching / grouped with 3 other circuits
8kw/230 Ib = 34.8A,
In >= Ib, 40A MCB
Cg = 0.75
Ca = 1 @ 30deg C
Cr = 1 as MCB
It = 40 / (0.75 * 0.55 * 1 * 1)
= 97A
OSG Cable selection from Table 6E1, page 123 = 25mm^2!!!
So practically, how is this value ever used?
8kw/230 Ib = 34.8A,
In >= Ib, 40A MCB
Cg = 0.75
Ca = 1 @ 30deg C
Cr = 1 as MCB
It = 40 / (0.75 * 0.55 * 1 * 1)
= 97A
OSG Cable selection from Table 6E1, page 123 = 25mm^2!!!
So practically, how is this value ever used?