Yes, I know but in the C&G example, the volt drop on 2.5mm² is very low so no need to have larger cable.So what you do is, get a figure for It, look up a cable size that has capacity of equal to or greater than that, find the voltage drop, calculate it, check against limits (<11.5V) and if bigger, go to next cable up. That's how you get the numbers.
A ring is two cables in parallel each of which is half the length of the circuit.Regarding resistance, when you say quarter, you mean because it's Line and Neutral lengths in parallel with Line and Neutral again to form the ring?
18 x 20 x 37 / 4 / 1000 = 3.32V
It works out the same 2 x 9 = 17 + 1.I'm not sure thats right as the length given is the length of the whole cable, not the middle of the ring.
Yes.Table F6 gives drop for a 2.5mm2 cable of 18mV,
The resistance of 2.5mm² conductors is 7.32 mΩ/mso this is for the line and neutral, so 9mV drop on each per meter, per amp. 9mV drop on 2.5mm2 wire gives a resistance of 0.009 ohms. A resistivity of 2.25x10-8, pretty close to pure copper of 1.77x10-8
7.32 x 1.2 (temperature adjustment for 70º) = 8.784 x 2 = 17.568 (the 18 value) mV/A/m.