I assume you mean their appliances use flex rated below 16A.I was making the point that if you go the continental way then you no longer have any protection related to the size of the flex.
Is that correct?
I suppose that must be considered satisfactory for a short inrush.Note that BS1363 does not require the fuse rating to be lower than the rating of the flex. For 0.5mm flex it says a 3A fuse should be used unless this poses a problem with inrush currents in which case a 5A fuse should be used.
Why do we fuse lighting circuits at 6A?For all other flex sizes it lists it says a 13A fuse is fine.
But not a 13A fuse with 0.5mm cable ?
I thought that was because internal wiring and flex drops were rated 6A.
You can do that here for fixed loads where the cable will not be overloaded providing the fault current conditions are met.In the rest of europe they seem perfectly happy to put 0.5mm flex on unfused plugs.
What happens when there's a fault ?
One explanation could be that in Britain the CCC of cables is vastly underrated.
I know it's not a straight comparison but 5A fuse wire has a CSA of just 0.03mm².