JCTucker said:
So whilst we are awaiting the answer on 2 or 3 core, another question!
I am not planning on running anything significant off the supply....a couple of lights, occasional power tool, and sometimes a heat lamp drawing 500W, and I am trying to avoid going to 25mm. Would a 16 amp circuit give me enough, in which case I think I can use 16mm, and be under the 4% drop threshold.....does this make sense?
Edited to say I need 175 meters
I don't think it makes any sense at all. 16mm² will put you on the edge for volt-drop, so if anything ever changed the requirements in the barn you'd have to re-dig a 175m trench, and replace 175m of cable. IMO, 25mm² should be the absolute minimum to consider, and that would only let you go to 30A. I've no idea how the cost ratchets up, but in your shoes I'd certainly look at how much difference 35mm² would make to the overall project.
. . . . .
PME?
PME??
I dunno - next you'll be telling me that I should read original posts properly..
Anyway - don't think I was ever dead set against it - it always seemed to me to be a topic rife with differing opinions and no consistent answers.
There's a good article about this in this quarter's Wiring Matters
† - last time I looked it wasn't online yet. The key factor is whether or not the detached building contains any extraneous-conductive-parts (see
this for a definition).
If not, exporting the earth is fine. If it does, then you should either make it TT, or extend the equipotential zone to the outbuilding by applying main bonding to the e-c-ps. It does seem perverse not to make every effort to keep a low EFLI if you can.
Q: - if you did go that route, would the use of 4-core SWA, with one core as the main bonding conductor be OK?
†Well worth subscribing to, BTW - free to anybody who asks
http://www.iee.org/Publish/WireRegs/questionnaire_new_update.cfm