There was an article, where it was pointed out some sizes of SWA the earth using the SWA was not good enough, I saved the bit below. 240 mm² is about the largest I have worked with, so using the armour has never been a problem.
Extra from John Peckham article on using the armour of SWA cable.
Table for 70°C Thermoplastic PVC SWA cables.
Conductor
CSAMinimum
CSA of SWA
to meet 54.7CSA of
armour 2 coreCSA of
armour 3 coreCSA of
armour 4 core1.5 3.4 15 16 17 2.5 5.7 17 19 20 4 9.0 21 23 35 6 13.6 24 36 40 10 22.6 41 44 49 16 36.1 46 50 72 25 36.1 60 66 76 35 36.1 66 74 84 50 56.4 74 84 122 70 79.0 84 119 138 95 107.2 122 138 160 120 135.3 (131) 150 220 150 169.2 (144) 211 240 185 208.6 (201) 230 265 240 270.6 (225) (260) 299 300 338.3 (250) (289) (333) 400 403.9 (279) (319) (467)