Try wiring the receiver using some cable and plug top, see if it works then.
 
Sponsored Links
Though a 3-core cable runs from the boiler to the Honeywell CM907 thermostat, the SwL isn’t connected at the Honeywell
believe that I need to connect the existing L & N from the boiler to the L & N of the Hive and the SwL to the Heating On (Terminal 3 ) of the Hive.
despite there being 230 volts at the L & N pins there
Did your original CM907 wiring look anything like this?:
Screenshot_20230109-211841_Chrome.jpg
 
Yes, exactly like this!
I'm afraid, that's the problem!
In the above image, the brown is live and the blue is switched live.
You don't currently have a neutral.
What is tricky - you would still measure 230V from the live, to the switched live.

If you can find where the cable connects to the boiler, you need to make the wire that wasn't connected (what you thought was switched live) into a neutral.
Post some photos of the connections to confirm. :)

Then DO NOT connect L&1 on the hive, the existing 2 wires go to 1&3 on the hive, do NOT put 240v in there, it might be connected to 24V at the other end and it will be a very expensive mistake if you get it wrong
I was writing the above as you posted - it is definitely worth checking, but as 230v was measured across live and switched live, I suspect it may be ok.

But again... Post some pics of the boiler connections!
 
Well I have just reconnected the Honeywell so that we have heating and hot water for the morning and thankfully it is working .

I will send some photos in the morning but I looked at the wiring connections yesterday and there is a 3-core cable connected to the L, N & SwL 230V control terminal blocks in the boiler (as attached image). The SwL is connected at the boiler but not at the Honeywell. The Earth isn’t used.
 

Attachments

  • 7404C2DF-E302-4331-89BB-D69895250DEA.jpeg
    7404C2DF-E302-4331-89BB-D69895250DEA.jpeg
    393.6 KB · Views: 71
Herewith some photos of the wiring inside the Atag boiler and the Honeywell that I took before I started.

As you can see, the boiler installer used the earth of the 3-core as a SwL and marked it as such with brown felt-tip at the boiler end only. This seemingly however was never connected at the Thermostat and just left bare.

Also, the Atag terminal diagram, marked-up with the wiring connections that I tried last night without success.
 

Attachments

  • B558158A-171C-46E7-BCB6-A43BD50A0BBB.jpeg
    B558158A-171C-46E7-BCB6-A43BD50A0BBB.jpeg
    2.2 MB · Views: 81
  • 0C871842-E53A-400D-B5CB-6251ACA5A565.jpeg
    0C871842-E53A-400D-B5CB-6251ACA5A565.jpeg
    188.1 KB · Views: 80
  • FF9C280D-910C-4B2C-BFAD-34F68BB51043.jpeg
    FF9C280D-910C-4B2C-BFAD-34F68BB51043.jpeg
    205.2 KB · Views: 76
Last edited:

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top