Correct. If it were part of a ring, there would be two cables connected to the 'feed' terminals (and one to the 'load' terminals'. The FCU is therefore probably a spur from somewhere. I suppose is still could be from that double socket if it, too, has cables to/from it going all the way up the wall (do you have solid floors?). Another possibility (although probably unlikely) is that the 'downstairs sockets' circuit is not a ring at all - but, rather, a 'radial' circuit. In that case, there would only be one 'feed' cable. What is the rating of the switch/MCB in your CU for that circuit (does it have something like 'B32' or 'B20' written on it)?Ah, ok - I guess the fcu can't be directly on the ring then, because there are only two cables going into the fcu, not three. One goes into the 'feed' terminals and the other into the 'load' terminals.
Fair enough. As you say, that confirms both that the FCU is feeding the 'bare cable' and that the FCU is (somehow) connected to the 'downstairs sockets' circuit.The fcu is definitely connected to the bare cable, as I wired it into a socket temporarily and checked it with a lamp. I also checked that the lamp went on and off with the other sockets in the room when the switch on the CU labelled 'downstairs sockets' was flipped, so I know they are on the same circuit (and it also went off when I turned off the switch on the CU labelled 'RCD' circuits, which I presume means they are protected by a circuit breaker).
As above, unless the 'downstairs sockets' circuit is a radial one (fairly unlikely), it must be a spur from somewhere - possibly from that double socket, possibly from somewhere else! If that's the case, then the FCU would be 'a spur off a spur', which is not compliant with current regulations. If it were a radial circuit, then there would be no compliance problems, provided the cables were of an appropriate size in relation to the breaker in your CU.Does that mean it is a spur, after all?
Kind Regards, John