I suppose that bonding in a bathroom would have a purpose if the "Eathing" on a bit of exposed metal failed to remain conductive.
Only if they are connected to the same earth, and by a low impedance.If Metal bit A is connected to "Earth" and Metal bit B is also connected to "Earth" then Metal bit B will be at the same potential as Metal bit A
That's the whole point - a metal part in a bathroom could have a substantial voltage on it when a fault occurs, but without bonding, another metal pipe entering from outside would not have that same voltage, and a dangerous potential would exist between the two items.The bonding of Metal bit A to Metal bit B would only serve a useful purpose if "Earth" was not at the same potential as "Earth"
Exactly. If "Earth" were not in inverted commas, but were just a 'single point', then everything connected to it would be at the same potential (if no current were flowing through the 'connections').Basic electrical theory seems to be excluded from the matter of bonding, If Metal bit A is connected to "Earth" and Metal bit B is also connected to "Earth" then Metal bit B will be at the same potential as Metal bit A .... The bonding of Metal bit A to Metal bit B would only serve a useful purpose if "Earth" was not at the same potential as "Earth"
a metal part in a bathroom could have a substantial voltage on it when a fault occurs
Yes, as well as the RCDs, the disconnection times must be complaint and Main Bonding must be satisfactory, again IF required.The circuits are RCD protected, so supplimentary bonding in the bathrooms, being 'omitted' is not an issue, am i right to suggest that this is ... provided disconnection times happened within set times.
It's also the MCB disconnection times - as RCDs are 'additional' protection, although they may be the only protection device.Before establishing whether RCD disconnection is within limits,
I suppose it would, but that is up to you. Will there be any fixtures with exposed-c-ps, if not then complying with the so-called 'future proofing' is also up to you.would it be prudent to lay wiring in preparation for bonding any extraneous-c-ps and exposed-c-ps, in case it is needed and before walls are closed.