Hi Guys,
Hope you can help me with a problem on the above boiler
The problem noticed first was that the hot water was not getting as hot as it used to, it starts off hot and then only lukewarm.
When standing next to the boiler i notice that when a hot tap is opened it seems to go through all the correct procedures and then the pilot light will go out and cut back in after approx 30 seconds?
I also noticed that the central heating fires up and then cuts out after 2/3 seconds and then will not fire up at all?
I have checked the ch sensor which gives me a reading of 3.6kohms the dhw sensor gives me 8.4kohms and the ch overheat gives me 0.005ohms.
I have also taken off the microswitches to reveal the brass plungers underneath and both of these operate correctly!
Anybody got any ideas please?
Regards
Chumley