3 year old boiler. Customer reported poor hot water flow.
Checked burner pressure to find boiler is not modulating on CH or DHW. Burner pressure does not move from about 2 mbar.
21mbar available at inlet to GV. Suspected NTCs, Gas Valve, PCB
NTCs are fine: have run with spares outside of boiler and still getting minimum burner.
Checked voltage to modulating coil: Max is 7v DC. Min is 2v DC.
Thus assumed fault to be with gas valve so changed it.
Alas not the case. PCB seems to be the only other possible fault, although this appears to be giving the correct voltage.
I am suspicious. All help or suggestions appreciated.