Agile said:gas4you said:I would be suprised if you really have a 21mbar working pressure on a combi unless it has been fitted by a 'perfect' installer who knows his pipe sizing inside out and your meter working pressure is 22mbar!
I saw a nice new changed regulator giving 21 mB with a 28kW load !
Pity about the gas pipe though. The cowboy installer had left the 15mm under the floor and it was losing 2.5 mB from the meter. I had an interesting advice to give to the owner.
All installers have to be perfect because CORGI are very hot on pressure loss and if they find over 1 mB will serve a defects notice as well as turning the boiler off saying its At Risk. It does not make the installer look good to the owner.
A friend of mine was caught on that and had to pay £100 to appeal which was a waste of time and was made to retake ACS pipe sizing module. That could have been costly but the training centre he uses let him do that free and issued him a letter saying he had completed it satisfactorily.
Tony
kktoday said:Burner pressure does not move from about 2 mbar.
The op has never taken the working pressure and clearly stated so near the start of the thread!
baxpoti said:kktoday said:Burner pressure does not move from about 2 mbar.
ollski wrote
The op has never taken the working pressure and clearly stated so near the start of the thread!
A friend of mine was caught on that and had to pay £100 to appeal which was a waste of time and was made to retake ACS pipe sizing module
kktoday said:Working pressure reveals the problem to be in the pipework. Not the meter unfortunately. Realized why I hadn't checked working pressure initially - screw on nipple done ridiculously tightly.
Paul Barker said:kktoday said:Working pressure reveals the problem to be in the pipework. Not the meter unfortunately. Realized why I hadn't checked working pressure initially - screw on nipple done ridiculously tightly.
Love it when the whole thing comes out and you have to sit around waiting for the ESP to turn up.
I had a gas leak once which went like, smell of gas, but put guage on test nipple, no drop at all. Turned out to be a crack in the nipple which was obscured by the guage tube whenever anyone did a tightness test. It had fooled another gas fitter Transco (as they were called at that time) and me at first.
kktoday said:To clarify.
22mbar standing P at meter. 21 standing P at boiler.
2.5 working P at boiler. 21 working P at meter.