here we go
1) "If you decide to service your boiler yourself, it is a good idea to get a new rubber seal that fits round the heat exchanger/combustion box base, and a new combustion chamber cover seal"
Seals are re usable and you need to be RGI to break the seal let alone replace!
2) "To start with, switch off the electrical supply to the boiler (it is not good enough just to switch the timer off, as the boiler will still have mains on it). Turn off the gas supply to the boiler. "
Why turn off the gas supply? the zero govenor gas valve won't open if there is no power supply. Where are your electrical checks?? positive isolation? earth continuity? resistance to earth? polarity? fuse rating?
3) "Before removing the combustion chamber cover, arrange a hook to support it, as there are wires on it and it is not advisable to let the cover hang on the wires. "
personally i just remove the spade connectors from the electrodes. Safes me using a "hook"
4) "Clean the tray thoroughly along with the condensate trap, which has a removable lid. "
Condensate trap has a removable lid? i suppose you glue it back on afterwards?
5) "I’m pretty sure that the howling or trumpeting sounds are caused by the seal between the lower tray of the combustion chamber and the main body being leaky owing to corrosion of the mating surfaces. It may require a suitable sealant to ensure an airtight seal. "
more like the is sediment in the heat exchanger water ways or the gas valve is partially blocked
6) "Nothing that has been done should have compromised the integrity of the gas carrying parts so there should be no leaks. Nevertheless it is good practice to check for leaks, so turn the gas supply on and listen and sniff around for any leaks. It is highly unlikely that any will be found, but if a leak is suspected, test with soapy water. If a leak is found, turn off the supply and contact a registered gas fitter. As stated before, a leak is extremely unlikely but it is best to be safe. "
omg lets break this one down
a) you have compromised the integrity of the gas carrying parts but removing the gas pipe from the gas valve to the fan venturi. 2 gas joints. 2 breaches of the law.
b) listen and sniff for leaks????????? i won't even go there
c) use soapy water? LDF is non corrosive. Soapy water is
7) "switch the power back on and turn the gas on"
turning the gas back on to the appliance. Where from? if it is at the gas valve isolation cock then you need to ldf. Is it is from the meter? Then you need to be RGI to re establish a supply.
"The flame should be a blue colour and the top of the burner will be glowing red"
looking for a blue flame on a premixed burner????? Doesn't matter what the colour is pal. Try using a gas analisyer to check if the CO/CO2 are through the roof after your cowboy service.
"Hopefully, lockout and howling will now be things of the past"
I agree as you will be 6ft under
Not one mention of safe isolation, working pressures, Gas Rate, CO/CO2 ratio.
See my above post