I can see the pin coming out and making the switch, also I have manually activated the switch and checked resistance with a multimeter.
No flame lockout ever.
According to the fault finding procedure which comes with the boiler it is looking like either incorrect gas pressure/gas valve setting, faulty gas valve or borked PCB.
Since installers have to always power flush a system on installation the manufacturers fault finding advice does not comtemplate a blocked plate HE and focus of failed components.
The real world is different! 80% of boiler faults on cheaper models are blocked plate HEs and other sludge related problems.
It is cutting out on central heating too so I don't think it is just the HE since central heating has its own larger one.
Some more info for you, sometimes when the central heating tries to come on the yellow ignition led lights for a fraction of a second but instead of the gas igniting the system 'clonks',the led goes out and the fan stops.
Sometimes it will try again after a few seconds and usually succeeds to ignite the gas.
It's looking like an intermittent temp sensor, before it was reading fine but now it has gone open cct...unless this is just a coincidence, you never know!