A friends baxi was causing him problems.. When heating was on and he'd turn a hw tap on.....the hot water would get hot(we'll come back to this). But when he'd turn tap off the boiler most of the time wouldnt go back to heating. Unless he'd turn tap on/off then it would kick back in.
Ther divertor was from NATIONAL HEATING SPARES and they told him they had no more in stock but send it and they would recondition it as it was in warrenty. I took it apart and the brass that connects to the by pass the non return bit wouldnt retract propally without help. Anyway hed had loads of problems with parts from ebay that were sticking etc. So naturally we thought this was the only problem.
He said there was a improvement in something or other but i noticed the hot water would cut out then kick back in ....repeatedly.
Id already checked sensing pipes for partial blockages when valve was out . So i removed the connectors from the 2 thermisters and put two test thermisters on. (connected to wiring but just sensing air as i didnt have time to fit them.
The boiler stayed on
I put the hw connecter back on the original thermister and it stayed on.
When i put the ch connector back on the original thermister boiler started cutting out again.
So it got late and i didnt have time to isolate and drain boiler. So my next step was to change out the ch thermister. Im pretty sure it isnt going to sort my cycling.
no1: existing thermisters read within tolerances when testing...4k both. which is why i dont suspect problem is thermisters, but with electronics anything is possible.
no2: I think the boiler will just cycle still due to insufficient flow or partial blockage causing boiler to cycle.
Can Anyone expand on this?
Pump was running so i guessed its between blockage in secondry hex or insufficient flow from pump?
Ther divertor was from NATIONAL HEATING SPARES and they told him they had no more in stock but send it and they would recondition it as it was in warrenty. I took it apart and the brass that connects to the by pass the non return bit wouldnt retract propally without help. Anyway hed had loads of problems with parts from ebay that were sticking etc. So naturally we thought this was the only problem.
He said there was a improvement in something or other but i noticed the hot water would cut out then kick back in ....repeatedly.
Id already checked sensing pipes for partial blockages when valve was out . So i removed the connectors from the 2 thermisters and put two test thermisters on. (connected to wiring but just sensing air as i didnt have time to fit them.
The boiler stayed on
I put the hw connecter back on the original thermister and it stayed on.
When i put the ch connector back on the original thermister boiler started cutting out again.
So it got late and i didnt have time to isolate and drain boiler. So my next step was to change out the ch thermister. Im pretty sure it isnt going to sort my cycling.
no1: existing thermisters read within tolerances when testing...4k both. which is why i dont suspect problem is thermisters, but with electronics anything is possible.
no2: I think the boiler will just cycle still due to insufficient flow or partial blockage causing boiler to cycle.
Can Anyone expand on this?
Pump was running so i guessed its between blockage in secondry hex or insufficient flow from pump?