Thanks John,The regulations don't actually require that the cables are more than 50mm from the surface - merely that, if they are buried less deep than that, that the circuit must be be RCD protected (which it quite probably already is). What the regs do require (unless you want to jump through various hoops) is that buried cables be routed within 'safe zones' - essentially horizontally or vertically in line with visible electrical accessories (FCUs, switches, sockets etc.).
Kind Regards, John
I thought that's what they might say. i could only find things referencing to older regs but did find a couple of things agreeing with you and EFLImpudence which through me. All cables will be within safe zones. I plan on mounting the FCU next to the socket I am spurring from on the horizontal and then the first switch will be vertically above it and then the second switch will be on the horizontal to the first.
Thank you for all your help will post a photo once the job is complete.