Hmm, I'd missed that reference, Ding
So thats taken from BSEN61008 and BSENEN61009 requireing operation at 2x in 150ms (which explains the setting on bans tester)
One would assume that there ought to be some testing done to make sure the device meets the BSEN (though I'd assume if you'd tested at 1x and 5x and both were sub 150ms then 2x will be as well?)
The regulations refering to supp. prection against direct contact and carelessness by morons bearing power drills don't reference 2x though, only 5x, unlike the table of disconnect time, which references the 2x parameter in relation to TT systems, I suppose you could also argue that the 2x parameter is not relevant to TN systems? (just thinking out loud here)
Talking about 2x in TT systems, its not a solid thing it would seem, what its trying to get at it seems, is a fault similar in magnatude to one thats likely to occur, and its quite likely that 5x would be a better choice than 2x in a lot of cases?
some discussion here:
http://www.theiet.org/Forums/forum/...5&threadid=22453&highlight_key=y&keyword1=rcd
Also interesting is the megger site here:
http://www.megger.com/uk/story/Index.php?ID=233
makes no mention of a 2x RCD test and states that all their instruments met the testing requirements of BS7671:2008 despite the fact that some of their most popular instruments lack a 2x setting
hmm... whens GN3 due out? I have a feeling we won't know for sure what exactly is required until then....