I have a Biasi Riva Compact HE and it wont spark.
The symptoms are the boiler is switched on and the fan fires for about 0.25 seconds then cuts outs. The pump is running and the flow switch engages correctly. The diverter valve can be heard to move across and sounds like its working ok.
I have checked the following:
Main Circuit Flow Switch works and the micro switch makes on the multi meter.
Both Temp probes are reading 13ohms.
Fan reads 43ohms.
Pump is slightly low at 218ohms against 230ohms nominal
DHW Flow Switch Red LED lights on DHW demand.
Flow Switch diaphragm cleaned.
Pressure Gauge Working @ 1.5bar.
No apparent leaks on sealed chamber.
Test ports at top are tight.
PCB fuses checked and no sign of dry joints.
No visible fluid or obstruction in condensate trap.
On draining the main circuit the water was clean and in good condition
I wired the fan directly to the mains by pulling the leads from the PCB connector and the fan runs well and I can hear the APS working and it shows as working on the multi meter.
As the APS can be heard working I have assumed the venturi is clear.
There is no boiler lockout light but there is a fault light on the left hand light bank of one solid green right hand LED and the middle red and left green LED's are flashing at about once every second.
Please could you give me some pointers. I assume its either the APS or the PCB at fault.
I am unsure of the start sequence but I think that the PCB checks if the APS is closed before it starts the fan, then checks for flow and if all is ok sends the ignition signal.
Any help would be appreciated.
Many thanks.
I have a Biasi Riva Compact HE and it wont spark.
The symptoms are the boiler is switched on and the fan fires for about 0.25 seconds then cuts outs. The pump is running and the flow switch engages correctly. The diverter valve can be heard to move across and sounds like its working ok.
I have checked the following:
Main Circuit Flow Switch works and the micro switch makes on the multi meter.
Both Temp probes are reading 13ohms.
Fan reads 43ohms.
Pump is slightly low at 218ohms against 230ohms nominal
DHW Flow Switch Red LED lights on DHW demand.
Flow Switch diaphragm cleaned.
Pressure Gauge Working @ 1.5bar.
No apparent leaks on sealed chamber.
Test ports at top are tight.
PCB fuses checked and no sign of dry joints.
No visible fluid or obstruction in condensate trap.
On draining the main circuit the water was clean and in good condition
I wired the fan directly to the mains by pulling the leads from the PCB connector and the fan runs well and I can hear the APS working and it shows as working on the multi meter.
As the APS can be heard working I have assumed the venturi is clear.
There is no boiler lockout light but there is a fault light on the left hand light bank of one solid green right hand LED and the middle red and left green LED's are flashing at about once every second.
Please could you give me some pointers. I assume its either the APS or the PCB at fault.
I am unsure of the start sequence but I think that the PCB checks if the APS is closed before it starts the fan, then checks for flow and if all is ok sends the ignition signal.
Any help would be appreciated.