I haven't got a clue what the input and output temperatures are.
OK. Have you got the boiler thermostat set to Max and does the return pipe feel cooler than the hot? If you can obtain/borrow a thermometer it would give a better idea. The difference should be 11°C (20°F)
By bypass, I assume that would be the hall radiator which hasn't got a thermostatic valve on it - unless there's another pipe/valve somewhere.
No, the hall rad is not the bypass. If you have one, it will be a pipe, immediately after the pump, which connects the flow to the return and has a valve on it to regulate the flow. Your boiler does not specify a bypass, so I doubt if you have one.
I think the boiler fires continually. It doesn't shut off and rest after an hour or so which would imply that the return water is still not hot enough for it to have a rest.
Boiler thermostats usually measure the
flow temperature. So, if the boiler is running continuously it is never reaching temperature. Is the boiler set to Max temp?
When I balanced the rads, I closed the valve (lock shield) on each rad about 1/2 way on those that were hot and left them open on the colder ones upstairs.
Ah, that could be where you are going wrong
- Set the system so only CH is on (no HW)
- Open all lockshield and rad wheel valves and remove heads from TRVs.
- Adjust the pump speed so you get approx 11°C drop at the boiler.
- Shut down boiler and pump
- Close all lockshield valves
- Open lockshield valve on rad nearest the pump 1/4 turn and check the temp difference between flow and return pipes of the rad is 11°C.
- If the diiference is too big, open the valve a fraction (no more than 1/4 turn)
- Of the difference is too small, close the valve a fraction.
- Repeat 6-8 on each rad in turn, moving away from the boiler
- Check the boiler temperatures are OK and adjust pump speed if necessary
- Replace and adjust TRVs to give desired room termperature
You may have to go round a couple of times to get everything correct - but don't aim for perfection. The important thing is to realise that it's only the first turn from closed on a lockshield valve which has any real effect.
I didn't know the 15/50 had 3 settings so I can't check at the moment what it is set to. Do they make a big difference?
Yes, if the pump is too fast it will be taking the water away faster than it can be heated, and vice versa. Your boiler needs a flow rate of 38 litres/second to deliver 29.3kW (100k BTU) with an 11°C temperature drop.
the plumber ... seemed to do it in an hour or so
So it wasn't a power flush then? If so, the flushing solution needs to circulate for at least two days and preferably as much as 4 weeks.
If you want to do it your self,
- Buy two cans of Sentinel X400 and two of X100.
- Drain and flush the system with plain water
- Refill with water, adding the X400
- Leave to circulate for several days (no more than 4 weeks)
- Drain and flush the system with plain water
- Refill with water, adding the X100
If any rads feel particularly cold at the bottom, they may be sludged up. You can help dislodge this by hitting the rad with a rubber hammer. You can also close down the other rads so the water only circulates through the problem ones. As a last resort you could remove the rad and flush through with a garden hose.