Hi mandate
I agree with what you say.
When I originally said that the switch is made when the lever is pushed all the way across, I was explaining to saintgeorge the difference between two test he did, and he could not understand why. He thought it was a sequence problem.
remember, his water heating only was always ok.
Now :-
ref the testing of the C heating with water off at the timeswitch..
In one test he switched on the C heating at the timeswitch, and made sure that the room stat was calling . The boiler didn't fireup on its own but did so when he pushed the lever to the right and went off again when he released the lever.
In another test with the water heating still off and C heating turned to off at the timeswitch, he latched the lever in the manual notch probably thinking that this was the same as pushing the lever to the right . then when he went and turned the heating on at the timer the boiler did not fire up . As I said earlier he was puzzled as the two results were different and he expected them to be the same , ie the boiler to fire up.
My statement that has caused the controversy was my explanation that the difference was that when the lever is pushed to the right a switch is operated which fires up the boiler. That statement is perfectly true. The fact that the switch transfers a little further to the right than where the lever in the notch was holding the quadrant , but actually before the lever is at the extreme right is irrelevant.
I agree with what you say.
When I originally said that the switch is made when the lever is pushed all the way across, I was explaining to saintgeorge the difference between two test he did, and he could not understand why. He thought it was a sequence problem.
remember, his water heating only was always ok.
Now :-
ref the testing of the C heating with water off at the timeswitch..
In one test he switched on the C heating at the timeswitch, and made sure that the room stat was calling . The boiler didn't fireup on its own but did so when he pushed the lever to the right and went off again when he released the lever.
In another test with the water heating still off and C heating turned to off at the timeswitch, he latched the lever in the manual notch probably thinking that this was the same as pushing the lever to the right . then when he went and turned the heating on at the timer the boiler did not fire up . As I said earlier he was puzzled as the two results were different and he expected them to be the same , ie the boiler to fire up.
My statement that has caused the controversy was my explanation that the difference was that when the lever is pushed to the right a switch is operated which fires up the boiler. That statement is perfectly true. The fact that the switch transfers a little further to the right than where the lever in the notch was holding the quadrant , but actually before the lever is at the extreme right is irrelevant.