Depends on what output your boiler has been set at, here is the figure for the highest output.

Capture.PNG
 
Yeah rtfm! I did that and it wasn't obvious to me.. :(

But I did read that table as the required flow rate when burner is lit.

What about minimum flow rate to protect against overheat, when the burner is off?

Basically, I'm trying to size a suitable TacoSetter inline valve..
 
Sponsored Links
The tacosetter is the wrong valve, you need a bypass valve like the Honeywell du145.
 
I don't want an ABV as pump is going to be a variable speed variety.

Either way, is 22.8 l/min the minimum flow to avoid overheat when not calling for heat?
 
Do not put a variable speed pump on a fixed output boiler, if you want to stop it over heating when the zone valves shut put in an automatic bypass,

or do want you want as you don't seem to take advice to well.
 
Ok, so what's your issue with variable speed pumps and fixed output boilers?
 
Your boiler has a fixed output of around 17kw, so it needs 23 litres per minute running through it to stop it overheating, you want to stick a variable speed pump that could go considerably lower than this, what do you think will happen ?
 
Your boiler has a fixed output of around 17kw, so it needs 23 litres per minute running through it to stop it overheating, you want to stick a variable speed pump that could go considerably lower than this, what do you think will happen ?

Ow ow I know I know pick me
 
Can we go back a few steps and ask why you want a variable speed pump?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Sponsored Links
Back
Top