I've never trusted that calculator. Best to do it room by room with a couple of online radiator suppliers.
I got about that figure as well!I have tried the boiler size calculator, which told me I need a 48Kw boiler
I haven't been able to get that low.I have tried redoing it a few times and keep getting slightly different results, but all in the low thirties Kw.
So you have a 24kW boiler feeding 24kW of rads in a large house. That would seem to be OK. But there' are two problems:My set of 16 radiators comes out as follows:
Stelrad Elite 50t - Total Watts 23516
Does that indicate that there will be a capacity issue for my Greenstar System 24i boiler, or does it still point towards balance as being the cause for the three of four highest radiators in my house not getting fully warm?
So you have a 24kW boiler feeding 24kW of rads in a large house. That would seem to be OK. But there' are two problems:My set of 16 radiators comes out as follows:
Stelrad Elite 50t - Total Watts 23516
Does that indicate that there will be a capacity issue for my Greenstar System 24i boiler, or does it still point towards balance as being the cause for the three of four highest radiators in my house not getting fully warm?
1st Problem
The boiler is designed to run with a temperature difference between flow and return of about 20C at max output but the radiator data is based on a 10C difference 75C/65C. If you want the same output with a 20C difference the rads will have to be run with an 80C flow and 60C return.
The problem then is that the boiler will not be condensing (the return temp has to be below 55C for condensing to occur). So we set the flow temp to 75C and return to 55C. Fine, but the radiator output will reduce to 85% of the figures given in the catalogue. SSo you would have to put in rads which are about 20% "oversized" to get the required output
2nd Problem
The boiler has a built in pump, which has an available head of 2m to pump the water round the heating circuit. The available head takes into account the pressure loss through the heat exchanger, which increases as the flow rate increases. If the boiler is run with a 10C difference instead of the expected 20C, the pressure loss through the heat exchanger will be higher so, instead of having 2m of available head you could have only 1m. In a house your size with the number of rads you have the required head could be over 2m. It all depends on how the system was designed and the pipe sizes used.
Balancing will certainly help.I assume the first step is still to ensure the radiators are correctly balanced - is that right? And then consider these issues from there.
The reason the top rads go cold when the downstairs rads are on is partly a balance problem, but also due to the pump not being able to deliver the water to the upstairs rads. Balancing with a higher differential will help.is it relevant at all that the problem top floor radiators get hotter to some degree if some lower floor radiators are turned off/down, and are coldest if all the lower floor radiators are turned on?
The problem is that each rad will be giving off less heat, so each room will be affected. Now this may be OK in some rooms if the rad is already larger than needed for the actual heat loss.To see if I understand point one, is this saying that even if all the radiators were correctly balanced, if it was operating efficiently I would need to add another couple of radiators in order to get the full 24kw of heat that the boiler is able to produce (as each rad would only output 85% of its potential as long as system was set up to enable the boiler to condense properly)? It may be an option for me to add a rad or two if advisable.
The basic problem with the upstairs rads is balancing. Yes, when correctly balanced each rad will be giving about 15% less than expected.However, is this issue likely to be any kind of cause of the problem with uppermost radiators (only) not heating fully? The way I read it was that a perfectly balanced system would mean than all my radiators heated up, but not to their maximum capacity (the balancing would mean that the total shortfall of c. 15% would be evenly distributed between all the radiators). Is that right?