Just to clarify, I have a Y plan system controlled by Hive. Room thermostat for CH and tank thermostat for HW. Separate time programmes for CH and HW. No outside compensation. Boiler is set at 65 degrees. HW tank set for 60 degrees.
Is your cylinder unvented? Are you sure?
What is the make and model
An unvented cylinder would in almost every case have a 2 port motorised valve to stop flow to the cylinder when desired temperature has been reached.
A midposition valve can under certain conditions make a false demand on the boiler
A midposition valve would not result in almost steep temperature rise unless the valve is open to radiator port and all radiators are closed.
Easy enough to find out why you are having issues by carrying out on site temperature distribution check
Your boiler is set to 65 and cylinder to 60. Try raiding the boiler temperature to 70 or 75. My money is on the cylinder not reaching desired thermostat set temperature so boiler keep firing, very little heat lost to load and boiler shutting down.