Central heating output of the boiler is from 9.9 - 28.0kW
Designed temp rise 20 degrees
Minimum flow rate for heating is 360 l/hr
To obtain a ΔT of 20°C between flow and return you will need a flow rate of around 950l/h around your system - With your current setup (21.75kW & 500l/h), there will be 38°C ΔT between flow/return during the first 15 minutes (mathmatically speaking).
The maximum ΔT you would achieve when the boiler modulates down to it's minimum 9.9kW would be 17.4°C (with your 500l/h flow rate).