There is a very marked difference in the two trends, the one immediately below is exactly as I would expect on recycle, ie the flow&return temps merge shortly after the recycle starts but the bottom trend (from post #26) is different with the flow&return temperatures falling in steps over time?
The parameters difference is I think that the bottom trend is with d.2, the recycle set time set to 60 minutes and the top trend additionally has d.1, the pump overrun time extended from10 minutes to 20 minutes, is this correct??
My understanding is that the pump runs continuously during the recycle period (with pump overrun having no effect) and the pump runs for the overrun time and then stops when all zones programmed off or all stats satisfied.
You might try it with d.1 returned to its original setting and see does the trend then revert to looking like the lower one.
View attachment 338029
View attachment 338028
I think your seeing a data capture timing issue in the bottom one as the capture of flow and return were at different times. I've sorted the issue out in the top one so there should be only a couple of seconds between the measurements.
The lines at the bottom of the chart give radiator, UFH and HW cylinder demand (from thermostats) plus the power going to the internal pump. I've also been able to capture the pump speed (grey line) which looks like it is 100% on ignition for 30sec then 45% the rest of the time
Still trying to find the right EBUS parameters to capture the rest of the boiler information. The pump on/off on the chart isn't correct as it comes on after the power is switch on to the pump and goes off when the burner goes off. It would be good if I could find the status message parameter to see which mode the boiler is in