Hi
I have a problem with my Potterton Prima F gas boiler. The overheat stat pops out almost daily. I have turned the boiler stat down to almost off and it still happens. I ran the heating this morning and measured the flow temp from the boiler. It got to 82 c before the boiler stat shut down the boiler and after cooling it fired back up again when the flow pipe temp was 38c.
After firing for this second time, the boiler flow pipe temp reached 84c before the boiler stat shut it off. There was no overheat stat pop out however.
I then turned the boiler stat up to 2 and the flow reached 84c before the boiler stat shut the boiler off again. It then fired up at 55c. I kept measuring the flow pipe temp, it got to 84c and the overheat stat popped out.
So the boiler stat setting seems only to affect the firing temp and not the final temp. Is this the way these thermostats usually operate? And is 84c too close to the overheat stat trip temperature? I appreciate the overheat stat measures the temperature of the boiler and not the water but I would have thought that turning the boiler stat down would lower the temperature at which it shut the boiler off and avoid these nuisance trips.
Any advice would be appreciated.. If any more info is needed, just ask.
I have a problem with my Potterton Prima F gas boiler. The overheat stat pops out almost daily. I have turned the boiler stat down to almost off and it still happens. I ran the heating this morning and measured the flow temp from the boiler. It got to 82 c before the boiler stat shut down the boiler and after cooling it fired back up again when the flow pipe temp was 38c.
After firing for this second time, the boiler flow pipe temp reached 84c before the boiler stat shut it off. There was no overheat stat pop out however.
I then turned the boiler stat up to 2 and the flow reached 84c before the boiler stat shut the boiler off again. It then fired up at 55c. I kept measuring the flow pipe temp, it got to 84c and the overheat stat popped out.
So the boiler stat setting seems only to affect the firing temp and not the final temp. Is this the way these thermostats usually operate? And is 84c too close to the overheat stat trip temperature? I appreciate the overheat stat measures the temperature of the boiler and not the water but I would have thought that turning the boiler stat down would lower the temperature at which it shut the boiler off and avoid these nuisance trips.
Any advice would be appreciated.. If any more info is needed, just ask.