Gas advice, tut tut tut
Advice?
No. its an instruction.
If you have gas leak, turn the gas off.
Gas advice, tut tut tut
Unless a leak this big is outdoors I'm sure he'd have smelled it by now.Advice?
No. its an instruction.
If you have gas leak, turn the gas off.
Unless a leak this big is outdoors I'm sure he'd have smelled it by now
But it seems the boiler is still working. If it passed gas for a while and then ignited there'd be a bang!It might be un-burnt gas venting out via the flue.
Gas valve passing gas but no ignition.
( Yes I realise that in theory this cannot happen, the controller ( PCB ) would not allow it to happen. But PCBs and gas valves can go faulty )
But it seems the boiler is still working. If it passed gas for a while and then ignited there'd be a bang!
In any case if he divides his figures by 2 (see #23) I doubt he has a problem. Between 11 Nov and 11 Jan I used 488 m3, about 5500 kWh, very similar to OP's usage.
Hang on - since this time in November is 2 months, not one. And there have been some cold spells.
Did you mean 50 kWh for the previous month, not 500? Edit - ignore that, I was confusing the daily with the monthly (or 2-monthly) figure.
OKSorry, that was a typo, the 5500 kWh was since December 12th.
Not sure, maybe the experts can comment. I'd just say the gas pressure at the burner is (most likely) adjustable, and it's possible the service guy increased it. That would increase the gas flow, but you would expect the heat into the water to increase also, so little effect on daily consumption. And I'd be surprised if it made the difference you're seeing.I suppose my question is, is it possible for boilers to burn more gas than they should for a given output? Is it burning so hard that excess heat is being pumped out of the flue (more so than normal) can a 15kw boiler burn twice a much if the gas valve is set wrong?
Sorry, that was a typo, the 5500 kWh was since December 12th. The actual bill landed today, closer to 5600 kWh since my confirmed and accurate reading on 12th December, 183 kWh per day according to bulb. It’s usually closer to 50 kWh per day in the cooler months, perhaps a bit higher when really cold. But not over three times higher.
I suppose my question is, is it possible for boilers to burn more gas than they should for a given output? Is it burning so hard that excess heat is being pumped out of the flue (more so than normal) can a 15kw boiler burn twice a much if the gas valve is set wrong?
Gas leak?
Check your meter whilst the gas appliances are all off?
No, flow varies as square root of pressure drop, so at 12 mb, approx 1.5 x flow at 5mb.If a burner burns successfully @ 5 bar and also @ 12 bar would it be using a little over twice as much gas?! Could the servicer have increased the pressure to the boiler? I'm by no means a gas/boiler expert just trying to understand.
Have.a.think.