That is true.As you say, the regs do not prescribe a test of whether or not something is an extraneous-c-p, but they do define a test of the adequacy of supplementary bonding, and I thought you had been known to suggest that this test can also be used to determine whether supplementary bonding is required (i.e. whether a part qualifies as 'extraneous').
The 'problem' (if there is one) is that the regs do not seem to explicitly recognise that 'passing' your ">23kΩ" (which, as you say, is arbitrary) is necessarily an acceptable means of demonstrating that something is not an extraneous-c-p (and therefore does not require SB). In other words, the 'problem' is probably that the regs do not define 'liable to introduce a potential' in a manner similar to that which your test attempts to do.Why is that a problem? ... That is why supplementary bonding may be omitted when RCDs are fitted. ... However, should the resistance be between 1667 and 23,000 (or 46,000) then supplementary bonding would still be required.The problem with that one is that "Ia" can be 30mA for an RCD or, say, 160A for a B32 - so that the maximum permissible resistance can be 1667Ω or 0.3125Ω !!
You will see that BAS has somewhat thrown a spanner into the works, by illustrating that the water in a short 'plastic interruption' is probably enough to result in a failure of your ">23kΩ test".
Kind Regards, John