Borrowing a live

Joined
27 Dec 2006
Messages
665
Reaction score
11
Location
London
Country
United Kingdom
I've messed up and only pulled a 3 core & earth to location of wired programmable room thermostats. This means the there is only power to these when the main programmer is calling for heat in that zone... Annoying when you want to make a change at the thermostat when programmer is off.....

My question..... If labelled clearly as to what it is, can I borrow a perm live from a lighting circuit?

Thanks
 
Sponsored Links
Sponsored Links
, can I borrow a perm live from a lighting circuit?
Certainly not.

If you really must have a programmer and a programmable thermostat, they can be made to work with a relay.
Permanent power to the thermostat, switched output from the thermostat powers a relay coil, the relay contact switches the output from the programmer.

The real solution is to sling the programmer away and just use the thermostats.
 
Current taken from the Live conductor of a circuit absoloutely *MUST* be returned to the neutral of the same circuit. Not doing so can be very dangerous to anyone working on the installation.

If the device has "volt free" contacts then technically you could supply the device from a local power source, while using it to switch stuff that forms part of the heating system, but if you do this then you need to fit warning notices to warn people that the equipment is fed from multiple sources. I would not reccomend doing this on a domestic heating system, it goes strongly against the principle of least surprise.
 
Just to play devil's advocate and further my own understanding, presumably there is nothing wrong from a wiring perspective with say a programmer being on one circuit and a thermostat being on another? Each device would be powered by the live on that circuit and returned to the consumer unit along the neutral of the same circuit. Be a poor design though not being able to turn off all the central heating devices with a single mcb. Although what about the immersion - that would likely be on a separate circuit. Hmmm....
 
Just to play devil's advocate and further my own understanding, presumably there is nothing wrong from a wiring perspective with say a programmer being on one circuit and a thermostat being on another? Each device would be powered by the live on that circuit and returned to the consumer unit along the neutral of the same circuit.
Right.

But what do this "programmer" and "thermostat" control and how do they control it? If they are switching mains voltage circuits fed from a different source to the one supplying the programmer then there needs to be an appropriate warning notice. Which then leads to practical considerations about where and how to affix said warning notice (and whether people will actually read it).

If they are switching ELV or sending wireless signals this is less of an issue.

Be a poor design though not being able to turn off all the central heating devices with a single mcb.
Agreed.

Although what about the immersion - that would likely be on a separate circuit. Hmmm....
IMO this comes down to "principle of least surprise". People expect all the controls on a domestic central heating system to be fed from the same place, people don't expect imersion heaters to be fed from the central heating system.
 