Hi, a friend has the above problem where either of his showers will trip the cu's only rcd/isolator. The mcb's for each shower don't trip
If I disconnect one of the heater elements from either shower both showers will heat the water.
If I switch the elements round both showers still work.
So the combined load of both heaters in either shower cause a trip.
If I disconnect both shower earth cables at the pull switches both showers still cause the trip on high setting.
All visible cables look OK and are tight.
I can't test insulation as I don't have the test equip so have told friend to get a elec in.
Just wondered do you think it could be a faulty main switch/rcd? Or is it more likely to be an earth fault somewhere?
Not now looking to fix this ....just interested.
Cheers,
Si.