Matey, you are going to have to do some serious sorting out if you try installing a "17th edition" board with dual RCDs and there's a borrowed neutral.
Before installing a new CU you should be doing a PIR and sorting out serious issues before you do the swop.
What would you do, for instance, if you found the measured value of PFC current exceeds breaking capacity of protective device or high values of EFLI on a circuit?
Would you then install the replacement CU and mark the departure on the EIC?
Where's your judgement on this, where's the line that you would draw.
If a borrowed neutral is OK what about no bonding to a gas service? Is a reversed polarity OK?
Just pop in on the cert as a non compliance, I'm sure the client will read it and understand the implications. Good grief