Apologies if this has already been discussed during my absence ...
We have often had discussions about the ‘acceptability’ of connecting a local earth electrode to a a TN installation, with at least some people suggesting that it is ‘not allowed’ (particularly with TN-C-S).
In response, many of us (including myself) have pointed out that a number of major countries require a local earth electrode (again, particularly with TN-C-S), that such an electrode offers an additional degree of protection and that, in any event, to ‘not allow’ an earth electrode to be connected would be ridiculous, given that there is a requirement to bond extraneous-c-ps to the MET of a TN installation.
Anyway, if I’m reading it correctly, it seems that we are probably about to join those ‘other countries’, since this appears in the BS7671:2018 DPC ...
Have I interpreted this correctly? If so, it might be Christmas for those who manufacture earth electrodes! Whist it’s straightforward for standard houses and many commercial premises, I wonder how this will work with multi-floor blocks of flats and office blocks?
Kind Regards, John
We have often had discussions about the ‘acceptability’ of connecting a local earth electrode to a a TN installation, with at least some people suggesting that it is ‘not allowed’ (particularly with TN-C-S).
In response, many of us (including myself) have pointed out that a number of major countries require a local earth electrode (again, particularly with TN-C-S), that such an electrode offers an additional degree of protection and that, in any event, to ‘not allow’ an earth electrode to be connected would be ridiculous, given that there is a requirement to bond extraneous-c-ps to the MET of a TN installation.
Anyway, if I’m reading it correctly, it seems that we are probably about to join those ‘other countries’, since this appears in the BS7671:2018 DPC ...
”BS7671:2018 DPC” said:542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2. Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.
Have I interpreted this correctly? If so, it might be Christmas for those who manufacture earth electrodes! Whist it’s straightforward for standard houses and many commercial premises, I wonder how this will work with multi-floor blocks of flats and office blocks?
Kind Regards, John