Thanks. That all makes total sense. I can also fully understand that (once earthed) it 'can and should' be treated as TN-C-S. However, my inquisitive mind still wonders whether it actually is (in terms of definitions) TN-C-S?The provision of an earth electrode is the absolute responsibility of the DNO. It does not form part of the customer's installation as it is directly connected to the neutral within the cut-out. If this is in place the supply can and should be treated as TNCS.
Perhaps more to the point in relation to some of the disussions here, I presume that (since 'M' would be only 1), although effectively TN-C-S, this is not regarded as PME? That could, as EFLI has been saying, be relevent in relation to the BS7671 requirements for the minimum CSA of main bonding conductors.
Since it ends up as 'effectively TN-C-S' as far as the installation is concerned, do I take it that the only reason PNB is used is to avoid the problem of separating (or combining) HV and LV earth electrodes in the vicinity of the transformer?
Kind Regards, John