As for the rest, I agree with everything you say about the vagaries of Ib for socket circuits, and the problems which a designer faces when trying to determine what it is, or what value he should use. ... Which is why I asked you what value you were using. And you said you were using 26A.
Well, what I meant was that the
instantaneous load was potentially 26A, but ....
There is no special exemption in 433.1.1 for socket circuits, and what you were designing for was a known case of simultaneous loads which you as designer judged to be an Ib of 26A. What if the dryer and the kettle were not plugged in but were each hardwired into FCUs with flex outlets? From an electrical and a regulatory POV nothing changes.
As I've just written to DS, I personally see the specific example we're talking about as a situation of 'diversity' - and, as you know, the regs themselves say absolutely nothing about when and how diversity can/should applied, so I feel free to make my own judgement about that. As I wrote, an occasional 2-4 minutes of an extra 13A has almost no impact on the average demand on the circuit as measured over any reasonable period of time. I suppose, therefore, that I asked for your response by answering your earlier question incorrectly - whilst I would have to regard the instantaneous load as potentially being 26A, I would
not regard that as the 'design current' for such a circuit, since I would 'apply diversity' when attempting to estimate the design current (I
b). If, in estimating that diversity, one assumes that the dryer (13A) is on continuously and that the kettle (13A) is on for 3 minutes every half-hour, that would represent an average load (which I would take as the 'design current' for that particular setup) of about 13.65A. Indeed, even with the ludicrous assumption that the kettle was going to be on for 15 minutes of every half-hour, even that would still only be an average current of about 19.5A.
So, in that specific case, I would have no problem (using my judgement about diversity) to protect a circuit which I 'knew' would only ever be used to supply a kettle+dryer circuit with a 20A OPD. In the real world, if there were also other sockets, goodness knows what I would regard as a realistic estimate of 'design current'. As I've said, proper design of sockets circuits is impossible, which is why we rely on OPDs to protect cables against 'the unexpected'!
Kind Regards, John