So it doesn't.As for earthing it, I'm sure one could find a way, but some might argue that (surprisingly) 522.6.101(iv) doesn't explicitly say that 'mechanical protection' (as opposed to sheathing, conduit, trunking or ducting) necessarily has to be earthed
Now there's a thing.
And now I come to think of it: "...sufficient to prevent penetration..."
Not "resist". Not "prevent reasonably foreseeable".
Just an unqualified, absolute, "prevent".
I wonder how you could protect a cable in a way which prevented any nail, any screw, any 'and the like' from penetrating the cable no matter how it was driven into the wall.
For 522.6.101(iv) to be complied with there would not be able to be any way known to man to drive a nail or screw or the like through the protection into the cable, no matter what materials, force or technology was used.
I don't think they thought that one through very well.