Just run through a past exam paper June 2022.
The last question is, as usual, a cable calc.
I was pretty close to the right answers on most of it. However two things threw me, when I checked the anwer sheet.
We've been taught that for a basic radial power circuit, You find the Ib (design current), select a protective device to get In. Then apply C factors for temp, thermal insulation, grouping etc etc. to get It. Then you look up the next size cable in the tables, taking into account installation reference method, etc. to get Iz.
In the answers sheet, their calcs take It and apply the Ca factor to it. This gives a different answer to mine.
I'm fairly sure I'm right and they are wrong but I'm only going on what we've been taught....
For more info, here's the question:
Their answer says to use a 32A breaker, then look up table 4D2A to find a suitable cable, they say 36A. Then they apply a Ca of 0.94 to get Iz of 33.84A
I think the correct answer is 32A breaker, apply 0.94 Ca factor to get 34.04A. Table F5(i) OSG shows Ref method C 2 core 36A capacity 4mm2.
The final result is not really much different but the calcs are not right.
Maybe the fact that the cable size is already identified in the question is the reason?
The last question is, as usual, a cable calc.
I was pretty close to the right answers on most of it. However two things threw me, when I checked the anwer sheet.
We've been taught that for a basic radial power circuit, You find the Ib (design current), select a protective device to get In. Then apply C factors for temp, thermal insulation, grouping etc etc. to get It. Then you look up the next size cable in the tables, taking into account installation reference method, etc. to get Iz.
In the answers sheet, their calcs take It and apply the Ca factor to it. This gives a different answer to mine.
I'm fairly sure I'm right and they are wrong but I'm only going on what we've been taught....
For more info, here's the question:
Their answer says to use a 32A breaker, then look up table 4D2A to find a suitable cable, they say 36A. Then they apply a Ca of 0.94 to get Iz of 33.84A
I think the correct answer is 32A breaker, apply 0.94 Ca factor to get 34.04A. Table F5(i) OSG shows Ref method C 2 core 36A capacity 4mm2.
The final result is not really much different but the calcs are not right.
Maybe the fact that the cable size is already identified in the question is the reason?